nope ev chargers get their own breaker box always, same with stuff like solar panels
2026-03-14 18:16:34
16
alec :
I mean, you can have many chargers, but you need to get ones that communicate and that will load balance. Meaning that if you use 2 tesla chargers, connect them wirelessly and they will communicate and share 48A from the same circuit
2026-03-14 01:12:28
17
Mpxceptional :
So it’s not a Tesla problem.
2026-03-15 02:17:54
100
jenny :
yep and this is why I installed my own and looked up all the codes and checked everything. used a torque wrench and everything. I don't trust anybody I've been screwed over more than once. for example, when I moved into my newly built house I was having lights that were flickering randomly and some breakers tripping and it ended up being that the original electrician did not tighten the wires in the electrical box to the correct torque spec ended up with most of them being loose.
2026-03-17 18:03:33
2
down_with_dad :
You can have two of them, but you need to have one as the primary and the other as a secondary which is a PowerShare mode. It sets a maximum value say 50A and then it will never allow both to have more than 50A between the two. So each EVSE needs its own breaker to be safe. The installation manual from Tesla shows how to do it correctly. This is what I have at my house.
2026-03-14 21:11:46
2
definitelynotemma131 :
joey that is insane
2026-03-14 04:47:09
6
Scwigglyfry :
Always have an inspection double check your electricians work, its only an extra $50-$200 and worth it
2026-03-15 01:05:12
6
mrcleann101 :
should of hired a better electrician
2026-03-26 02:34:26
2
Charging Cycles :
Photo does not appear to be a melted circuit panel box.
2026-03-31 02:23:12
1
notblairwinter :
In my state they require a permit and an inspection. Did they have an inspector come out after your install?
2026-03-14 13:49:04
5
Mr H. Town :
I have two but i turned it down to 20amps
2026-04-12 20:00:21
0
Michael with an H :
I have 100A service and a Tesla charger on a 60A circuit, which allows 48A charging. Plenty power left for the rest of the house. 200A should be fine for two chargers, as long as it is wired properly to either share one circuit or have each on their own.
2026-03-31 05:16:38
1
john2456787 :
You can have 2 but they PowerShare which decreases the amperage to each
2026-03-15 19:18:54
0
user7578160490790 :
Pursue your electrician for compensation. Sue if necessary. A 200amp main circuit can more than adequately support two EV chargers running full bore at the same time. 200amp minus the 80% continuous run rating leaves 160amps for continuous running. It’s usual to install 60amp circuits for EV chargers resulting in 120amps. That still leaves 40amps continuous run for the rest of the house which is still quite a lot. Depends on your situation though.
2026-03-23 21:56:22
5
Papi Ralph :
Based off the photo and your explanation, the EVSE’s weren’t the cause of the fault. When melting occurs at the meter base or service entrance conductors, the most common cause is a high resistance connection such as a loose or improperly torqued lug, corrosion, or a damaged meter socket, not normal downstream load from EV chargers.
2026-03-16 04:15:32
1
Shitbox kingpin :
no reason to charge a max power for overnight charging. I do 20a@240v and it's almost always at my charge limit in the morning. Constant 96a is just reckless on residential systems
2026-03-31 22:58:41
1
Prime REI :
Always talk to a few electricians. Go with your gut, not all are great evens if licensed
2026-03-30 02:09:11
0
Grin Puzzle :
Thanks for the info. I need a second
2026-03-16 00:41:10
0
Josue :
Your service can support two, what looks like is that your electrician double tapped other circuits in order to make space for the the breakers, causing things to melt.
2026-10-01 07:51:17
0
Calvin817 :
sounds like you should have had a permit pull.
2026-08-11 22:18:53
0
Neel Ghetia :
Lmao this is why you go with certified installer
2026-05-25 05:24:50
0
RobbieP :
So glad you didn’t have a fire. License is important
2026-04-26 19:45:40
0
Sylvia :
We have 2 chargers. We hired a professional to install the 2nd one. It is more work for them and more expensive, but better safe than sorry 😬!
2026-03-18 16:29:26
2
To see more videos from user @joeyzabaglo, please go to the Tikwm