@tanner.the.electrician: What’s the difference between a Main Bonding Jumper and a System Bonding Jumper? Where does the System Bonding Jumper go? Let me know if you have any questions. #electrician #LearnOnTikTok #fyp #education #greenscreen
in the transformer is what we usually do in commercial
2026-03-19 16:14:29
6
rocknrider80 :
What is the portable generator then is that floating. You should do one on that portable generator with a transfer switch.
2026-03-19 16:56:33
0
sparkyjoel72 :
fun fact: if you hard pipe the separately derived system with a metallic raceway, the raceway becomes your supply side bonding conductor
2026-03-20 15:58:05
2
Wut :
In the graphic, is the emt for the primary side used as a ground? There’s no ground ran with the primary side wires.
2026-03-29 22:01:17
1
Dodgeinator :
In this example why isn’t there an egc coming from the line side? And if there was would you bond that to the metal enclosure of the transformer as well?
2026-03-21 15:25:18
0
Sparkydad :
In the transformer to building steel
2026-03-20 03:58:29
0
Oldskool85 :
Xo plus ground
2026-03-20 01:54:03
0
Master in Bama :
in the transformer if it's on the floor.
at the panel if the transformer is 30' in the air
2026-03-19 23:47:06
0
sparkyjoel72 :
I use the green screw that comes with the breaker panel
2026-03-20 15:55:01
0
derek the solarboi ⚡️ :
Btw, "Let me explain it in dum-dum terms" needs to be on merch
2026-03-26 19:04:55
1
Grayson :
Normally in the transformer we hit the case then through the XO then to the ground lug definitely over kill since you hit the frame 2 times but welcome to industrial
2026-03-19 21:49:42
0
bo220 :
👍👍👍
2026-03-20 00:52:38
0
love2HVAC :
👍
2026-03-20 15:18:42
0
To see more videos from user @tanner.the.electrician, please go to the Tikwm