@hvac_tips3: ​AC outdoor unit stopped working? 🛑 Check this FIRST! ​Testing an AC capacitor with a multimeter is super simple. Here’s how we verify 35+5 uf ratings in seconds. ​#HVAC #HVACLife #HVACtech #AirConditioning #DIYHVAC

HVAC_TIPS
HVAC_TIPS
Open In TikTok:
Region: US
Thursday 22 October 2026 22:30:32 GMT
2809
136
11
5

Music

Download

Comments

lonewolfe76
Brian Bartley :
I’d check high and low voltage first
2026-10-27 20:16:09
0
miracleghostrants
MiracleGhost :
is it also necessary to shut off the breaker
2026-10-23 00:42:10
0
tinman_5000
Tinman5000 :
I’d check for high and low voltage first, then work my way through the contactor. If voltage is good then i would move to capacitor. I’ve learned to chase where the failure is that way. But to each their own! Good cap video!
2026-10-22 23:17:37
1
nicholait92
Nicholai :
If the outdoor unit isn’t working the first thing you check is incoming power. Then check call. Then check capacitor. You go straight to the cap. Your little diagram showing what wire colors go where isn’t any good unless they have a carrier/bryant unit 😂
2026-10-24 02:37:43
0
shawneo37
Shawn :
I'm thinking I should check the sound of my video first
2026-10-25 14:02:57
0
paulmachado20
Paul Machado :
On a TXV system with low suction pressure and high superheat, how would you distinguish between low refrigerant charge and a liquid-line restriction?
2026-10-23 18:48:56
0
.don74
Don :
Check incoming voltage on line side. Check control circuit voltage. Then contactor. Of everything good, Evaluate capacitor next. My thought process.
2026-10-22 22:39:25